A 240-volt feeder supplying twelve 120-volt, 30A shore power receptacles requires a minimum ampacity of _____ amperes if the demand factor is 80%?

Prepare for Load Calculations Test with comprehensive questions on feeders and services. Engage with multiple choice questions, hints, and explanations. Gear up for success!

Multiple Choice

A 240-volt feeder supplying twelve 120-volt, 30A shore power receptacles requires a minimum ampacity of _____ amperes if the demand factor is 80%?

Explanation:
To determine the minimum ampacity required for a feeder supplying multiple receptacles, you must first consider the demand factor and the total load. In this scenario, you have twelve 120-volt, 30A shore power receptacles. 1. **Calculate the total load**: Each receptacle can draw a maximum of 30 amperes at 120 volts. For twelve receptacles, the maximum possible load would be: \[ \text{Total load} = 12 \, \text{receptacles} \times 30 \, \text{A} = 360 \, \text{A} \] 2. **Apply the demand factor**: The demand factor is typically a consideration that accounts for the fact that not all devices will be in use simultaneously. In this case, you're given a demand factor of 80%, which means you need to calculate 80% of the total load: \[ \text{Adjusted load} = 360 \, \text{A} \times 0.80 = 288 \, \text{A} \] 3. **Adjust for feeder capacity**: Since this is a 240-volt feeder supplying 120-

To determine the minimum ampacity required for a feeder supplying multiple receptacles, you must first consider the demand factor and the total load. In this scenario, you have twelve 120-volt, 30A shore power receptacles.

  1. Calculate the total load: Each receptacle can draw a maximum of 30 amperes at 120 volts. For twelve receptacles, the maximum possible load would be:

[

\text{Total load} = 12 , \text{receptacles} \times 30 , \text{A} = 360 , \text{A}

]

  1. Apply the demand factor: The demand factor is typically a consideration that accounts for the fact that not all devices will be in use simultaneously. In this case, you're given a demand factor of 80%, which means you need to calculate 80% of the total load:

[

\text{Adjusted load} = 360 , \text{A} \times 0.80 = 288 , \text{A}

]

  1. Adjust for feeder capacity: Since this is a 240-volt feeder supplying 120-